Boiler steam test special report
article by: John McMillan
Hot on the heels of our last report is the news of the boiler's
first steaming since 1964! Here's how we built up to that
momentous event.
We needed a successful hydraulic test of the boiler before it
could be steamed, so over three days in mid September the filled
boiler was connected to a compressor and pressure was gradually
raised, with attention given to any leaks as they occurred.
Eventually the pressure was raised to 330lbs p.s.i., slightly
higher than the Insurers' requirement. Although there
were a number of leaks, Chatham Steam stated that they were
starting from a very good position with no "fountains" and only a
few "squirters"! (I hope you can cope with the high-tech.
jargon!) They considered that most leaks could be sorted out
with just a few minutes' work.
On 1st October the Insurance Surveyor, Chatham Steam
and our representatives came together for the formal hydraulic
test. Once again the filled boiler was pressurised to 320lbs
p.s.i. as required, and with only a few tiny weeps from the fire
box corners the Insurance man declared himself satisfied with the
test. The first hurdle had been overcome. The boiler
was then drained down to deal with persistent leaks from the Belly
Plate and two Thermic Siphon washout plugs.
The out-of-frames steam test in front of the Insurance Surveyor
was fixed for Wednesday 18th November, so we arranged to
be on site at Detling on the Monday before. The first job was
to assemble the fire grate inside the fire-box. The grate had been
assembled in the open at Toddington, but this was the first time
we'd attempted to fit it within the confines of the fire-box.
We had some difficulty getting it all to fit properly, and some
fettling of the larger fire bars will be necessary before the loco
can enter service, but the fit was considered good enough for the
static testing at this stage. The fire hole doors were
brought out of storage and fitted up.
Water pressure at the Detling site is poor, and a hose had been
filling the boiler all day. By late afternoon a check on the water
level (using the 'high-tech' method of poking a finger in a washout
plug hole!) revealed that the water level covered the fire box
crown, and this was considered deep enough to light a warming fire;
the great moment had arrived! At 4.30p.m. on Monday
16th November 2009, the first fire since August 1964 was
lit in the boiler of 35006 Peninsular & Oriental S.N.Co.
The fire was fed with wood, banked up and left overnight.
On Tuesday morning the fire was out but the boiler was still
warm to the touch. After sorting out more water supply
problems, the fire was re-lit and fed slowly and steadily with wood
plus occasional bags of steam coal. By lunchtime, one of the
two safety valves had started to 'feather' with only 170lbs p.s.i.
on the pressure gauge. The safety valves are brand new and
we've had no chance to test or set their working pressures, so a
special spanner was used to adjust the valve to a higher
setting. Firing continued until the valve eventually lifted
at 185lbs p.s.i. with a huge roar and jet of steam. This had
two effects, one being our wild exhilaration at this historic
moment, and the other the emptying of surrounding industrial units
as people rushed out to see what all the noise and fuss was
about!
On the Wednesday, the day of the insurance company visit, one
safety valve was removed and the boiler, still very warm from the
day before, was re-lit and brought up readily to pressure. At
200lbs p.s.i., the valve started to 'feather', so the adjusting
spanner was used to tighten it down as far as possible. The
valve finally opened at 225lbs p.s.i., 10% below where it should
work (250lbs), but sufficient to satisfy the boiler inspector that
the valve was working satisfactorily.
The purpose of the test was to see how the boiler performed when
hot and under pressure. The inspector was particularly
interested to see if there were any defects in the boiler's
platework, paying particular attention to the joints between the
boiler plates. We haven't worked on any of these areas, so it
was nice to see that the original North British joints were still
steam-tight nearly 70 years after they had been made. We
continued firing gently to cycle the safety valve a few more times
and found that it worked consistently and smoothly. The
boiler inspector pronounced himself satisfied with everything he
had seen. On reflection, the boiler has performed better than
we could have hoped. We had no trouble raising steam with
very little fire and the boiler 'drew' beautifully, proving what a
superb steam raiser she is.
Now we have to ensure that the momentum is maintained, and the
final work on the boiler is completed as soon as possible so we can
get our precious asset back to Toddington. Then we will be
engaged in fitting up all the many components that have been
restored already, and a complete locomotive will gradually
emerge.
There is one stumbling block in this plan, however, and that
inevitably is money or the lack of it! The boiler work and
its return will seriously drain the coffers, and the skilled work
needed to complete the engine will cost money we don't yet have.
The rate of progress will be dictated entirely by the availability
of funds.
So if you feel like helping us to achieve our final goal by
purchasing some shares in our project from as little as £10 a
month, please get in touch and we'll be happy to give you details
of the share scheme.
If you would like more details, please write to:
35006 Locomotive Society
243 Botley Road,
Burridge,
Hampshire
SO31 1BJ